"Coleman Centrifical Switchstuck open" , posted Sat 3 Feb 04:16user profileedit/delete messagepost reply


This is a Coleman furnace Model #BDGATO90BDD Manufactured by EVCON of Kansas.
I have a signal light showing 3 flashes which states that the Centrifical switch is stuck open.
Just what does this switch do; and is there anyway to test it?

May God Protect Us And Keep Us Free!!!

 


Replies:

yuri

24.79.131.223

"Re(1):Coleman Centrifical Switchstuck open" , posted Sat 3 Feb 11:52user profileedit/delete messagepost reply


Do you know the age of the unit. The ones I have worked on have a switch in the end of the ventor motor to prove that it is running and allow the burner to fire. If it is sticking you should get a serviceman in to fix it as it is a critical safety device. You may have to replace the motor. I don't know if the switch is available seperately.

Hope this helps

Yuri

 

 

sheprr2174

71.227.92.234

"Re(2):Coleman Centrifical Switch stuck open" , posted Sat 3 Feb 19:55user profileedit/delete messagepost reply


The unit is about 10 to 13 years old.
I replaced the switch and motor it came as aone piece assembly.
The motor was vibrating very bad; this resolved that problem.
Thank You
sheprr2174

May God Protect Us And Keep Us Free!!!

 

 

yuri

24.79.131.223

"Re(2):Coleman Centrifical Switchstuck open" , posted Sat 3 Feb 11:57user profileedit/delete messagepost reply


The switch should close if the ventor motor is running. If the motor is seized up/ too slow/ or not running that is why.

Yuri