This is a Coleman furnace Model #BDGATO90BDD Manufactured by EVCON of Kansas. I have a signal light showing 3 flashes which states that the Centrifical switch is stuck open. Just what does this switch do; and is there anyway to test it?
May God Protect Us And Keep Us Free!!!
| | Replies:
|
| yuri | "Re(1):Coleman Centrifical Switchstuck open" , posted Sat 3 Feb 11:52  
Do you know the age of the unit. The ones I have worked on have a switch in the end of the ventor motor to prove that it is running and allow the burner to fire. If it is sticking you should get a serviceman in to fix it as it is a critical safety device. You may have to replace the motor. I don't know if the switch is available seperately.
Hope this helps
Yuri
|
| | sheprr2174 | "Re(2):Coleman Centrifical Switch stuck open" , posted Sat 3 Feb 19:55  
The unit is about 10 to 13 years old. I replaced the switch and motor it came as aone piece assembly. The motor was vibrating very bad; this resolved that problem. Thank You sheprr2174
May God Protect Us And Keep Us Free!!!
|
| | yuri | "Re(2):Coleman Centrifical Switchstuck open" , posted Sat 3 Feb 11:57  
The switch should close if the ventor motor is running. If the motor is seized up/ too slow/ or not running that is why.