"Amana GUIC HVAC Blower Problem" , posted Sat 3 Feb 10:18user profileedit/delete messagepost reply


The Anmana GUIC furance was installed about a year ago. It was running fine, but was very noisy. An out of state visitor that was familiar with furnaces opened up the unit, and somehow changed the blower settings. Now however, the unit runs but the blower is on an extremely low setting that is not acceptable for this time of year. Does anyone know how to change the blower settings? Thanks for your help.

Chilly in Georgia

 


Replies:

yuri

24.79.131.223

"Re(1):Amana GUIC HVAC Blower Problem" , posted Sat 3 Feb 11:41user profileedit/delete messagepost reply


Ideally you should get a serviceman in to change the blower speed AND check the temp.rise through the furnace. If it is too low the unit will cut out on limit and you will have lots of future problems. It should be serviced annually to clean the flame sensor etc.

Good Luck

Yuri

 

 

jane30066

24.98.141.229

"Re(2):Amana GUIC HVAC Blower Problem" , posted Sat 3 Feb 12:39user profileedit/delete messagepost reply


Thanks. I will contact a HVAC service man.

Chilly in Georgia