"Switching thermostats need help with wiring" , posted Sat 3 Feb 17:05user profileedit/delete messagepost reply


I had the honeywell pro 3000 thermostat and I just bought the Trane 800xl.

The old honeywell was straight forward

E- white wire
Aux - Black wire
Y - yellow wire
G- green wire
O - orange wire
L - nothing
R- red wire
B- nothing
C- power blue wire

The new trane 800xl

Had Y2
F
X2
W1
S1
S2
RC
R
O
Y
G
B

I hooked them up per what I could tell from the diagram as all the colors matching up and putting the back in X2 and the white in W1 but nothing ever comes on.

Please help

 


Replies:

Houston204



24.175.6.172

"Re(1):Switching thermostats need help with wi" , posted Sun 4 Feb 13:29user profileedit/delete messagepost reply


It looks like a honeywell touchscreen stat on Trane's website.
Did you turn off power to the furnace before replacing the stat?
You may have blown a fuse. Does the fan come on when you touch red to green?

 

 

ecupip

75.110.65.148

"Re(2):Switching thermostats need help with wi" , posted Sun 4 Feb 22:44user profileedit/delete messagepost reply


Unfortunalty I did not see a breaker in the main panel for one the only thing my system has is a box outside and one on the air handler that does not have a breaker or fuse inside but a black pull out that has it on if inserted one way and off if put in upside down. I pulled those and and put them back in but nothing. No fan with the red and green wire either. Would there be a breaker somewhere else?

Also do the colors match the lables?

The one thing good about it if I have burned something up it is a new house and still has warranty but I can't tell the builder I was trying to replace the stat nor ask him about the new one since they will know i did it then :-(

 

 

Houston204



24.175.6.172

"Re(3):Switching thermostats need help with wi" , posted Wed 21 Feb 00:56:user profileedit/delete messagepost reply


I mean a low voltage fuse. Usually a 3 amp (automotive type) fuse for gas heat or a 5 amp fuse for electric heat. It would be in your furnace if its 1992 or newer. If you don't have a fuse you need a 24 volt transformer. What kind of furnace do you have?

Looks right, Trane uses B for C (common). Be sure to jumper RC and R.