bryant - http://www.hvacmechanic.com/ Forums


Original message

curtisM

71.217.5.92

"bryant" , posted Sun 23 Sep 19:48user profileedit/delete messagepost reply


Originally set up as up flow the ac unit was installed on top of the furness. If I convert it to downflow will the ac unit sit on the plenum then the furness?

curtis

 


Replies:

Houston204



98.196.66.53

"Re(1):bryant" , posted Sun 23 Sep 20:18user profileedit/delete messagepost reply


The upflow model probably cannot be converted to downflow. Post the model number of your furnace for verification.

"Tip of the Day" Remember to remove power first.

 

 

curtisM

71.217.5.92

"Re(2):bryant" , posted Sun 23 Sep 20:40user profileedit/delete messagepost reply


350MAV048080 Ifound this info online Standard Features
4-way multi-poise design for upflow, downflow, or horizontal installation.
Factory configured for upflow. Hot surface ignition. Redundant slow opening gas valve. Monoport inshot burners. Selectable blower-on timer.
40-va transformer.
Multispeed, direct-drive PSC blower
motor.
Aluminized-steel primary heat exchanger. EverlasticTM Polypropylene-laminated condensing

curtis

 

 

chandler57

71.169.158.114

"Re(3):bryant" , posted Sun 23 Sep 20:51user profileedit/delete messagepost reply


go to www.bryant.com and look in their search window for your model number. You will find the installation manuel and it will tell you how to convert this unit to a down flow coil.