A/C runs continuously - keeps cooling - http://www.hvacmechanic.com/ Forums


Original message

sharkbite92

68.192.176.171

"A/C runs continuously - keeps cooling" , posted Mon 24 Sep 09:14user profileedit/delete messagepost reply


Replaced an old mercury thermostat with the Honeywell RTH230B programmable... I turned it to cool, and it just stays on and keeps cooling the house well below the temperature programmed. For example, I got up this morning, the A/C was on, the program called for 71 degrees and it was already down to 65...

Any ideas?

 


Replies:

centar



12.217.46.242

"Re(1):A/C runs continuously - keeps cooling" , posted Mon 24 Sep 14:51user profileedit/delete messagepost reply


I had the same problem but not because of changing the thermostat. Houston told me that my problem was caused by a short between the red wire and the yellow wire. He was correct, those two wires were shorted outside next to the heat pump. However, since you just changed your thermostat, your problem is likely to be in how you wired your new thermostat.

Houston will probably give you some excellent advice on this.

Just trying to keep cool while the power is still on!

 

 

Houston204



98.196.66.53

"Re(2):A/C runs continuously - keeps cooling" , posted Mon 24 Sep 19:17user profileedit/delete messagepost reply




List the terminals used and the color wire connected to each on your old stat.

I suspect that this stat is not compatible with your multistage heat pump.

"Tip of the Day" Remember to remove power first.

 

 

sharkbite92

71.251.197.2

"Re(3):A/C runs continuously - keeps cooling" , posted Wed 26 Sep 15:08user profileedit/delete messagepost reply


Well, it's not a heat pump, I can assure you of that...

Wiring, well it's a 4-wire system, red to Rh, white to W, green to G, and yellow to Y. There is also the jumper from Rh to Rc.

It's a normal system with a gas furnace and A/C.

But when I set the thermostat on cool it just keeps cooling. The thermometer on the thermostat is working, but it's just not turning it off when it's reached the programmed temp.

 

 

Houston204



98.196.66.53

"Re(4):A/C runs continuously - keeps cooling" , posted Wed 26 Sep 20:38user profileedit/delete messagepost reply


If this problem only occurs when you set your stat to cool, you need a new stat. If it always energized Y regardless of mode setting it could have been a short in your wiring, possibly behind your stat.

I wouldn't recommend anything below the Honeywell 5000 series.

"Tip of the Day" Remember to remove power first.