| Original message
| Replies:
|
| amech | "Re(1):Thermostat wiring" , posted Wed 16 Jan 17:30  
1 is good, 2 is better. Use 18/8 wire if available. Always good to have some unused spare wire conductors in the event you would need then. Ex: Shorted wiring, adding sensors, etc.
|
| | abellone | "Re(2):Thermostat wiring" , posted Wed 16 Jan 20:53  
I'll run two more wires. Can you tell me how to wire them as the original thermostat is only a one stage and the new one will be two stage? Do I hook up the existing wires the same, and if so, what does the new wire hook up to (at both ends).
Thanks
|
| | amech | "Re(3):Thermostat wiring" , posted Thu 17 Jan 17:51  
Typical Wiring( Furnace & Thermostat) Red = Rh & Rc (Jumpered at T-Stat) This is 24v Power. Green = G (Fan Circuit) White = W1 (1st stage heating) Orange = W2 (2nd stage heating) Yellow = Y1 (1st stage cooling) Blue = Y2 (2nd stage cooling is equiped) Black = C (common)
Hope this helps.
|
|
|