heat pump - http://www.hvacmechanic.com/ Forums


Original message

gaclements

65.5.252.128

"heat pump" , posted Sat 19 Jan 12:38:user profileedit/delete messagepost reply


This is Goodman PHJ030-1A. The unit will not go in to heat model. You know this unit default is cool. I check the reversing coil and found that I have 24 volts going to the coil, check the coil for ohms and found that it's 17.6 ohms, but the ohms can be from 17-60 ohms. Since the ohms are so low this could be bad. I didn't check it non-magnetic piece metal. I also didn't check for the amps. I have check coils to be alright but when put under load it wouldn't pull the plunger. I'm thinking this is the same case. What do you think?

[this message was edited by gaclements on Wed 23 Jan 22:04]

 

Replies: