Original message
| r247yan | "ruud furnace" , posted Mon 21 Jan 16:09  
Hello all
i am having trouble with my ruud 90 achiever plus furnace, It will start the inducer fan comes on and all then sneds signal to the dsi ( ignitor ) and the ignitor will click a few times and then does not light and goes into lockout for an hour. It is getting spark, i cleaned flame sensor & ignitor but with no avail. The if you turn power off and try again while Ignitor is SPARKING i blow across main burners and it lights no problem and runs til set temp is reached. Then same things happens.. I tryied to blow air from compressor to clean burners but no luck. Any ideas.. I am hvac certified but i do mainly new installs no service..
| | Replies:
|
| tinmantu | "Re(1):ruud furnace" , posted Mon 21 Jan 19:38  
those style of burners have to be pulled and thoroughly cleaned with compressed air...if you try to clean in place, it just blows more lint into the crossovers.
|
| acefurnacefxr 
| "Re(1):ruud furnace" , posted Mon 21 Jan 16:47  
did u take apart the pilot and clean the pilot orafice?
HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT
I have been performing HVAC repairs for 23 years
http://www.hillaryclinton.com
|
| | r247yan | "Re(2):ruud furnace" , posted Tue 22 Jan 00:15  
thanks for the info. i will try to take burners out, well i am sure i can get them out, the problem will be can i get them back in ... lol
ill try to keep you updated
|
|
|