"Furnace help" , posted Tue 22 Jan 10:25user profileedit/delete messagepost reply


We have central heat/air. The furnace burners come on but the fan comes on and then off about every 30 to 60 seconds. The filter is new. What could be causing the fan to cycle on and off so often?

 


Replies:

amech

68.79.168.58

"Re(1):Furnace help" , posted Tue 22 Jan 16:28user profileedit/delete messagepost reply


If the burners are coming on as well and going out 30 seconds or so. Remove and clean your flame sensor. It is located in front of the burners with one wire going to it.

 

 

thunderhead

68.92.139.131

"Re(2):Furnace help" , posted Tue 22 Jan 16:42user profileedit/delete messagepost reply


Thanks. After I adjusted the fan limit switch, and cleaning everything within reach, it seems to be functioning correctly.