"Direct Vent with Overhang??" , posted Sat 26 Jan 12:25user profileedit/delete messagepost reply


I plan on installing a Steling Unit heater in the shop. It is a seperate combustion type. One of the specs says the vent has to be 3 ft down from any overhang. The overhang on my shop is a bit less then 2 ft. It is a fan powered vent. Can the vent be extended to comply or is there any other trick thing I can do?? Idealy it would be down about 15 inches from the overhang.

Thanks for anyones help and insight here.

charlie

 


Replies:

yuri



207.161.220.42

"Re(1):Direct Vent with Overhang??" , posted Sat 26 Jan 12:48:user profileedit/delete messagepost reply


You may want to contact the manufacturer or distributor about that. All of those specs are there so you don't end up with swirling wind/pressure switch tripping problems and are field tested to work. Ignore them and you may have a problem. In my area the gas inspectors are EXTREMELEY picky and will measure that distance and compare it to the installation manual and not pass the installation.

Yuri

[this message was edited by yuri on Sat 26 Jan 12:51]

 

 

oboyu2

71.111.14.176

"Re(2):Direct Vent with Overhang??" , posted Sat 26 Jan 12:55user profileedit/delete messagepost reply


Thanks Yuri. I guess I can run it to the front of the shop and it will look pretty ugly but better that then dead!!