"york diamond 8 - 7 blinks" , posted Sat 26 Jan 20:09user profileedit/delete messagepost reply


We have a York Diamond 80. The unit does not come on. I have limited to no experience in this area. There is an indicator light which blinks 7 times. I think this means "lockout with no ignition - after three tries.

Does anyone have any thoughts or should we call a technician.

Soliz

 


Replies:

Felixs

68.94.218.55

"Re(1):york diamond 8 - 7 blinks" , posted Sat 26 Jan 20:36user profileedit/delete messagepost reply


We hear the gas open three times and you get a very slight smell of the gas. This happens three times then it shuts down. At no point do I ever see a flame. The furnace comes on, but there is no flame.

Thanks.

Soliz

 

 

Houston204



98.196.66.53

"Re(2):york diamond 8 - 7 blinks" , posted Sun 27 Jan 01:55:user profileedit/delete messagepost reply


Does your ignitor have any obvious physical damage?


"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Sun 27 Jan 01:55]

 

 

Felixs

68.94.218.55

"Re(3):york diamond 8 - 7 blinks" , posted Sun 27 Jan 09:28user profileedit/delete messagepost reply


H,

Yes, there does appear to be slight damage to the ignitor. It is a bit less than the image you posted. There is also a white/gray residue on the ignitor.

Is this easy enough to replace. At this point we have a contractor coming out tomorrow. Let us know what you think.

Thanks again.

Soliz

 

Houston204



98.196.66.53

"Re(1):york diamond 8 - 7 blinks" , posted Sat 26 Jan 20:18:user profileedit/delete messagepost reply


Reset power to your furnace and watch as it goes through it's paces.

inducer fan starts



Hot surface ignitor glows




Gas valve opens (usually hear a click)


Fan motor runs



If you see a flame at all burners and it locks out anyway, clean your flame sensor with steel wool or emery cloth. Do not use sand paper.

"Tip of the Day" Remember to remove power first.