| a4man4mbz | "Coleman Evcon model DGAT056BDC" , posted Sun 27 Jan 20:40  
I have a Coleman Evcon Model DGAT056BDC, Ser# 940366111, Every so often the heater will not blow warm. It blows out side air into the home, and with the temp outside at 28-36 degrees, it gets down right cold. Eveytime I pull the covers off to see if the pilot light comes on,heater works. I changed filters, checked for loose connections, only thing found was loose ground at the gas valve, wire runs from ignition module. Any Ideas, this heater does not have a diagnosic light.
a4man4mbz
| | Replies:
|
| mgussler614 
| "Re(1):Coleman Evcon model DGAT056BDC" , posted Tue 29 Jan 21:41  
i have worked on alot of this unit pull out the buner assembly and clean the flame sensor the unit is going to a lockout in the ingtion control module every time you turn the unit off it resets the board
guz 1
|
|
|