"bryant 395cav wont run" , posted Mon 28 Jan 13:53user profileedit/delete messagepost reply


I have a bryant 395 cav042091 furnace that wont run. thermostat calls for heat, main blower runs, draft inducer motor starts but quits running within a few seconds. I have done the component test and blower, draft motor, and hot surface ignitor all seem to work properly.

joemo

 


Replies:

wondering

216.82.171.6

"Re(1):bryant 395cav wont run" , posted Mon 28 Jan 23:34user profileedit/delete messagepost reply


The pressure switch got upgraded about three times, but it sounds like you are going to be upgrading the board. Check the heat exchanger first, cause the board is a ces expensive puppy.

 

341

99.246.83.83

"Re(1):bryant 395cav wont run" , posted Mon 28 Jan 16:33user profileedit/delete messagepost reply


Sounds like a pressure switch is stuck closed. It should be in a normally open position, then close when the ventor motor starts.

www.hvactechgroup.com

 

Freezone12



72.64.113.192

"Re(1):bryant 395cav wont run" , posted Mon 28 Jan 16:26user profileedit/delete messagepost reply


is the unit flashing any codes?

try cycling the power off for 5 seconds then back on and see if the problem goes away.