| joemo | "bryant 395cav wont run" , posted Mon 28 Jan 13:53  
I have a bryant 395 cav042091 furnace that wont run. thermostat calls for heat, main blower runs, draft inducer motor starts but quits running within a few seconds. I have done the component test and blower, draft motor, and hot surface ignitor all seem to work properly.
joemo
| | Replies:
|
| wondering | "Re(1):bryant 395cav wont run" , posted Mon 28 Jan 23:34  
The pressure switch got upgraded about three times, but it sounds like you are going to be upgrading the board. Check the heat exchanger first, cause the board is a ces expensive puppy.
|
| 341 | "Re(1):bryant 395cav wont run" , posted Mon 28 Jan 16:33  
Sounds like a pressure switch is stuck closed. It should be in a normally open position, then close when the ventor motor starts.
www.hvactechgroup.com
|
| Freezone12 
| "Re(1):bryant 395cav wont run" , posted Mon 28 Jan 16:26  
is the unit flashing any codes?
try cycling the power off for 5 seconds then back on and see if the problem goes away.