Honeywell RTH7000 wiring problem - http://www.hvacmechanic.com/ Forums


Original message

flyert

71.254.208.154

"Honeywell RTH7000 wiring problem" , posted Sun 3 Feb 17:47user profileedit/delete messagepost reply


I am replacing my old Honeywell LR69071 thermostat with a new Honeywell RTH7000 and I'm having problems with getting it to kick on. I assume the wiring is screwed up. I have a 3ton Comfortmaker heat pump that has 6 wires from 2 lead wires coming into the old thermostat. One lead has a green and yellow, while the other has a green, red, blue, and white.
Any help on how things supposed to get hooked up is appreciated.

 


Replies:

Houston204



98.196.66.53

"Re(1):Honeywell RTH7000 wiring problem" , posted Sun 3 Feb 18:32:user profileedit/delete messagepost reply




The LR number doesn't help. Post the Q674? ???? number on your old subbase.

I hope you labeled each wire (Or wrote down your old wire combination) to prevent the need to trace your wiring at this point.

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Sun 3 Feb 18:44]

 

 

flyert

71.254.208.154

"Re(2):Honeywell RTH7000 wiring problem" , posted Sun 3 Feb 20:30user profileedit/delete messagepost reply


Too late on labeling, I looked at it quick and thought it was color coded with the R, Y, and etc. but obviously I'm wrong.
Also the only markings that are on the thermostat are LR69071 and T841A1001, does that help any? I might have to retrace my wires now anyway. Like I said there's one lead wire presumably for air conditioning with 2 wires going to thermostat and the other has 4 going out to it for heat? Let me know if I'm seeing this right.

 

 

Houston204



98.196.66.53

"Re(3):Honeywell RTH7000 wiring problem" , posted Sun 3 Feb 22:28user profileedit/delete messagepost reply


http://customer.honeywell.com/techlit/pdf/68-0000s/68-0051.pdf

Your old X = C (common)

It used the same terminals as this T841A 1746...


This diagram might help you trace your wiring.


If I were to guess, I'd say that your 4 wire is...
G = green
R = red
X = blue
W2 = white

The 2 wire ...
Y = yellow
O = green

This should be verified at your air handler to avoid damage to your transformer, or worse. Both of those wire sets go to your air handler. From there they run out to your heat pump.

"Tip of the Day" Remember to remove power first.

 

 

flyert

71.254.208.154

"Re(4):Honeywell RTH7000 wiring problem" , posted Sun 3 Feb 22:37user profileedit/delete messagepost reply


Houston204, that's awesome feedback and that's exactly what wire combos I see. I'll let you know what happens tomorrow. Thanks again.

 

 

Houston204



98.196.66.53

"Re(5):Honeywell RTH7000 wiring problem" , posted Sun 3 Feb 22:49user profileedit/delete messagepost reply


It's that common wire that will do the damage if wired incorrectly. It is not very hard to trace it though.

The O wire is also in question.

If you can't figure it out, it may be cheaper to pay a tech.

"Tip of the Day" Remember to remove power first.