"ON one minute off the next then on 80U-19A" , posted Tue 5 Feb 00:53user profileedit/delete messagepost reply


The burners turn on for a couple of minutes and the blower runs and then the burners go out and fan stays on. The burners turn on again and repeat the same cycle. I will look at the thermostats heat anticipator to see if it is cycling on and off too quickly. Could it be the regulator or the overlimit switch?

Cali

 


Replies:

jbwstroker



71.219.223.194

"Re(1):ON one minute off the next then on 80U" , posted Tue 5 Feb 10:55user profileedit/delete messagepost reply


Could be. Check for dirty filter(s) or dirty flame sensor.

"I'd probably be considered an old wise man if I could only remember everything that I've learned".

 

 

bob2636

76.87.194.113

"Re(2):ON one minute off the next then on 80U" , posted Tue 5 Feb 11:46user profileedit/delete messagepost reply


The vent was blocked by the roofers.