"White-Rodgers 1F35-910 Replacement" , posted Wed 6 Feb 09:54user profileedit/delete messagepost reply


Trying to replace a White-Rodgers 1F35-910 thermostat and update with an electronic model. System is hydronic with zones; current wiring is a three-wire system, with R, Y and 4, connected to zone valves. One wire is the common, the other the call for heat (opens the valve) while the other calls for the valve to shut (call for cool?). Adding to this mess is the addition of a relay on two of the zones, which energizes separate wall-mounted fan units once the respective valve is open and de-energizes when the valve shuts.

WR only has two options - buy another 1F35-910, or upgrade to their $$$ electronic model. I don't want another bi-metal mercury model, and their electronic model seems to be overkill. Honeywell support recomments the RTH5100B, connecting the '4' wire from the WR thermostat to the W terminal. Supposing that works for the RTH5100B, is there any reason that it wouldn't work on any other thermostat with a 'W' terminal?

I'll add that these thermostats are used for heating only. AC was added to the house at a later date, and that system has it's own thermostat.

Any suggestions/recommendations would be appreciated! Thanks.

 


Replies:

tipokotpu

70.70.138.193

"cause to undergo1" , posted Sun 20 Apr 06:28user profileedit/delete messagepost reply


Hi
Sub domain web hosting
Free web hosting & domain
Free web hosting free domain name
Web hosting with domain name
Capital management debt collection
Bsi debt management

 

tipokotpu

70.70.138.193

"excuse2" , posted Wed 16 Apr 23:38user profileedit/delete messagepost reply


Hi all! ecommerce
Cheap ecommerce web hosting
Web hosting and ecommerce

Medical malpractice insurance carriers
Medical malpractice defense attorney
malpractice
Medical malpractice records
Statute of limitations on medical malpractice

 

Houston204



98.196.66.53

"Re(1):White-Rodgers 1F35-910 Replacement" , posted Wed 6 Feb 20:19user profileedit/delete messagepost reply


Any thermostat with a W terminal can work with the addition of a SPDT relay. (This is needed with energize to open / energize to close valves.)

The listed thermostats provide a normally closed cicuit which opens with a heating demand. This removes the need for an additional relay.


The Visionpro touchscreen lists this as a series 20.


It must be configured to do this. (Option 170 = 5)


"Tip of the Day" Remember to remove power first.

 

 

pdt1842

216.223.34.13

"Re(2):White-Rodgers 1F35-910 Replacement" , posted Mon 11 Feb 15:52user profileedit/delete messagepost reply


Thanks for your help. Was able to replace the WR thermostat with a Honeywell 87K, and they are calling for heat and opening/closing zone valves perfectly.