| theduke03 | "Re(1):Goodman Blower Speed" , posted Fri 8 Feb 22:28  
How can you use the temp rise method on a heat pump to calculate airflow? You can't. How could the air handler be moving too much air, especially on the slowest speed? That would be possible if the indoor and outdoor units were mismatched. Need more info.
You can't put a price on comfort! Be Safe.
|
| | k_in_in | "Re(2):Goodman Blower Speed" , posted Fri 8 Feb 23:42  
I used the temp rise method by turning off the heat pump and turning on the 10kw electric heating elements. This gives me a know input for the formula. With the heat pump off and only the 10kw elements on my temp rise was 20 degrees. It does not seem posible to me to have to much air flow, but I can not think of anything else that would keep the temp rise so low with the 10kw elements on. I figured I should be about 30 degree rise with this situation.
Thanks
|
| | dwcaveney | "Re(3):Goodman Blower Speed" , posted Sat 9 Feb 00:57:  
Prior post deleted by sender dwcaveney for the following reasons: inaccurate, presumptious, confusing and of no practical value. Please excuse me.