| ronboman | "Comfortmaker Theromstat with 8 wires" , posted Fri 8 Feb 16:44  
Trying to replace the old Comfortmaker T-Stat with a Honeywell CT70
Old T-Stat terminals be used W1 C G E R O T Y
Goodman Heat Pump. I can not find a wiring diagram that covers this many terminals? I have good pictures if needed. Any help would be welcomed.
| | Replies:
|
| Houston204 
| "Re(1):Comfortmaker Theromstat with 8 wires" , posted Fri 8 Feb 22:13  
Old = New W = W2 C = X G = G E = E R = R O = O T = tape off this wire Y = Y