"Cold Air" , posted Fri 15 Feb 07:35user profileedit/delete messagepost reply


I have an Arcoaire furnace that is about 10 years old that has been running pretty steady this winter (cold up here). I got up this morning, and my house was 54 degrees. The furnace was running, but blowing cold air. I took off the panel, and watched it cycle for awhile. Seems to be going through a normal ignition sequence, only the ignitor doesn't light up. I changed it 3-4 years ago, so I know it has been a problem before. Do you think it sounds like that could be the problem again? What is the life cycle on an ignitor for a furnace that runs pretty steady? Is there a way a can test it? Thanks.

 


Replies:

cjett

75.52.163.40

"Re(1):Cold Air" , posted Fri 15 Feb 09:04user profileedit/delete messagepost reply


If you have 120v going to the HSI but no glow, replace it.

 

 

bendb

72.135.126.62

"Re(2):Cold Air" , posted Fri 15 Feb 09:33user profileedit/delete messagepost reply


Sure enough, that's what it was.

Replaced and up and running.

Thanks!

 

 

cjett

75.52.163.40

"Re(3):Cold Air" , posted Fri 15 Feb 09:44user profileedit/delete messagepost reply


Glad to hear you have heat.