| Original message
| Replies:
|
| frost 
| "Re(1):comfortmaker RPJII furnace short cyclin" , posted Fri 22 Feb 20:48  
When you say it short cycles; do you mean: The fernace runs for a few mins and then shuts off, or it tries to start and then shuts down before it has time to ignite. How old is the unit and you know if it has an induce draft motor (exhust fan motor), this info will help me, to help you
Don't try to fix whats not broken!
|
| | popandcranky | "Re(2):comfortmaker RPJII furnace short cyclin" , posted Fri 22 Feb 22:29  
The furnace is from 1998. By short cycling I mean: the exhaust blower cuts on, the air pressure switch engages, and before the igniter is triggered the units shuts down. there is a short pause of 30 seconds, and then this happens again and again until you turn the stat to off. All these symptoms go away completely when the mechanical thermostat is installed. Here is the original post if that might help: http://www.hvacmechanic.com/forums/resservice/messages/27574.htm
thank you for your time.
|
| | mgussler614 
| "Re(3):comfortmaker RPJII furnace short cyclin" , posted Sun 24 Feb 16:31  
sounds like the pressure swich is opening before ignitor is coming on either the inducer motor orfice is pluged up or a clogged exhaust pipe or the board is going bad better call a pro
guz 1
|
| | popandcranky | "Re(4):comfortmaker RPJII furnace short cyclin" , posted Sun 24 Feb 20:45  
Why, then, would the symptoms go away when a mechanical thermostat is installed?
|
| | mgussler614 
| "Re(5):comfortmaker RPJII furnace short cyclin" , posted Tue 26 Feb 22:16  
you reset the power to the board when you turned of the furnace to put on the new tsat
guz 1
|
|
|