"Honeywell RTH230 will not shut off Furnace" , posted Thu 28 Feb 10:14user profileedit/delete messagepost reply


I hooked up a Honeywell RTH230 programmable thermostat to a oil furnace with the wires matching the red, green and white wires for the heat. Ever since hooking this up the furnace will not shut off unless the heat/cooling on off switch is moved to off. could the wires be color coded wrong and reversed or is the thermostat broken?

 


Replies:

Houston204



98.196.66.53

"Re(1):Honeywell RTH230 will not shut off Furn" , posted Thu 28 Feb 19:12user profileedit/delete messagepost reply


Did you remove power to your furnace before replacing the stat?

Does the gas also run, or is it only the fan?

Did your old stat use a C (common)?

"Tip of the Day" Remember to remove power first.

 