Original message
| msuspartan | "Lennox problem, Lights for 1 1/2 seconds..." , posted Sun 16 Mar 15:26  
I'm hoping this is some easy fix. I have a lennox 80UHG3-75A-3. I woke up this morning and the furnace was not on. I took the cover off, turned it off and turned it back on. The furnace looks like everything is going fine as it starts, stays on for 1 1/2 seconds and turns off. This will repeat for about 5 times before it stops trying again. I have been told it is not staying on because its getting some problem message internally? Anything easy I can look at to get it running again? Being a sunday its going to be hard to get someone to come out. Help please!!!!
| | Replies:
|
| Houston204 
| "Re(1):Lennox problem, Lights for 1 1/2 second" , posted Sun 16 Mar 15:43  
Clean your flame sensor with steel wool.
"Tip of the Day" Remember to remove power first.
|
| | msuspartan | "Re(2):Lennox problem, Lights for 1 1/2 second" , posted Sun 16 Mar 15:54  
I'll give that a shot! Thanks!!
|
| | msuspartan | "Re(3):Lennox problem, Lights for 1 1/2 second" , posted Sun 16 Mar 16:49  
You rock! It works perfect again. Thank you so much!
|
|
|