fan coil noise on Carrier - http://www.hvacmechanic.com/ Forums


Original message

polo

24.64.223.203

"fan coil noise on Carrier" , posted Sun 16 Mar 22:37:user profileedit/delete messagepost reply


the fan noise coming out of registers is quite high. we have a 4ton Carrier (Comfort)model FY4ANF048. the fan motor is 3/4hp. at the lowest setting.all ductwork to registers is 5"diameter. the noise is especially hard to take at night when unit starts.
how can we overcome this problem. forgot to mention, house is 3,176sq feet. air blows 4 to 6 feet out of registers.

[this message was edited by polo on Sun 16 Mar 23:20]

 

Replies:

dcdraftworks



69.105.125.131

"square grill" , posted Tue 18 Mar 23:32:user profileedit/delete messagepost reply


Try a higher velocity register grill without a diffuser. (less metal area than a stamped grill/diffuser) Some high velocity systems use no screen at all.

[this message was edited by dcdraftworks on Tue 18 Mar 23:34]

 

theduke03

24.250.19.62

"Re(1):fan coil noise on Carrier" , posted Mon 17 Mar 16:35user profileedit/delete messagepost reply


If your fan is on lowest speed and you can hear the air like that then your ducts are too small. That system is supposed to run on high or med-high speed for best performance and efficiency. All you can do is replace them with larger ducts or possibly add more ducts(if trunks are big enough). My company usu. only uses 5" duct for bathrooms, and other small rooms. I can't speak for your house but 5" ducts sounds quite brutal! You should call a good tin-knocker to evaluate the duct system.

You can't put a price on comfort! Be Safe.