| wmichgrad | "Wiring? - Honeywell T8411R to Hunter 44860" , posted Sun 11 May 15:42  
Hello.
I have a Honeywall T8411R that I am replacing with a Hunter 44860.
The Honeywell was wired as follows:
G C R Y jumpered to W1 W2 E O
I wired the Hunter as follows:
Old = New G = G C = C R = Rc/R Y = Y1 W2 = W2 E = E O = O
The A/C seems to work fine. However, the heat is not operating. The fan is not even kicking on. Any thoughts on the subject are appreciated.
Thanks!
Eric
| | Replies:
|
| | wmichgrad | "Re(2):Wiring? - Honeywell T8411R to Hunter 44" , posted Mon 12 May 13:11  
Thank you. Still did not work. Called Hunter tech support. Also had to run the jumper from R/Rc to RH, which was not indicated in the manual for heat pump.
Thanks again!
Eric
|
| | Houston204 
| "Re(3):Wiring? - Honeywell T8411R to Hunter 44" , posted Mon 12 May 20:39  
Thank you, I will adjust my diagram accordingly.