"Wiring? - Honeywell T8411R to Hunter 44860" , posted Sun 11 May 15:42user profileedit/delete messagepost reply


Hello.

I have a Honeywall T8411R that I am replacing with a Hunter 44860.

The Honeywell was wired as follows:

G
C
R
Y jumpered to W1
W2
E
O

I wired the Hunter as follows:

Old = New
G = G
C = C
R = Rc/R
Y = Y1
W2 = W2
E = E
O = O

The A/C seems to work fine. However, the heat is not operating. The fan is not even kicking on. Any thoughts on the subject are appreciated.

Thanks!

Eric

 


Replies:

Houston204



98.196.66.53

"Re(1):Wiring? - Honeywell T8411R to Hunter 44" , posted Sun 11 May 18:33user profileedit/delete messagepost reply


Yu must configure your stat for heatpump operation as described on pages 28 and 29.




"Tip of the Day" Remember to remove power first.

 

 

wmichgrad

68.112.64.165

"Re(2):Wiring? - Honeywell T8411R to Hunter 44" , posted Mon 12 May 13:11user profileedit/delete messagepost reply


Thank you. Still did not work. Called Hunter tech support. Also had to run the jumper from R/Rc to RH, which was not indicated in the manual for heat pump.

Thanks again!

Eric

 

 

Houston204



98.196.66.53

"Re(3):Wiring? - Honeywell T8411R to Hunter 44" , posted Mon 12 May 20:39user profileedit/delete messagepost reply


Thank you, I will adjust my diagram accordingly.