| kyblueeyes | "no air or heat coming threw vents" , posted Fri 23 May 23:38  
i have a tempstar 2 ton heat/ac pump, no heat or air coming threw the vents, but unit is running.
kyblueeyes
| | Replies:
|
| thechris333 | "Re(1):no air or heat coming threw vents" , posted Wed 28 May 09:13  
if the indoor unit is running but not the outdoor: 1. Your capacitor in the outdoor unit may be bad 2. Your condenser breaker may be trippped or off 3. The float switch for the condensate line may be tripped; if the line is backed up 4. If you take off the panel to the outdoor unit and depress the contactor and the unit comes on then you know that your problem is low voltage related (thermostat or circuitry)
chris
|
| Houston204 
| "Re(1):no air or heat coming threw vents" , posted Mon 26 May 00:47  
Is the indoor fan running at all?
If the motor is not running, but getting power and it spins freely when power is removed, you may only need a capacitor.
"Tip of the Day" Remember to remove power first.
|
| | kyblueeyes | "Re(2):no air or heat coming threw vents" , posted Wed 28 May 13:14  
there nothing come threw the vents, but unit is running outside when i turn heat or ac on just nothing coming threw the vents on inside, could it be the blower motor fan.
kyblueeyes
|
|
|