Original message
| futureafacadet | "trane baystat 239 to honeywell rth230 HELP!!!" , posted Sun 25 May 16:39  
I'm trying to switch from the weathertron baystat 239 to a honeywell rth230. I am having problems with the cooling coming on. It seems that its doing the opposite of what it says, when it says its cooling its really pushing out hot air. Then i can turn the cooling off and the fan will just work. I tried switching up the heating and cooling wires but nothing seems to work. HELP!
I took the Baystat 239 off and the wiring is as follows: 0(orange) X2(black wire connected) G(green) Y(yellow) T(tan) R(red) W(white) U(nothing was connected) F(nothing was connected) B(blue)
What wires do i put to which letters on the honeywell rth 230?
Rh-Rc (these two are jumped and i have the red wire to the Rc side) W-white Y-yellow G- green What am i doing wrong? please help my house is getting hot!!
| | Replies:
|
| | Houston204 
| "Re(2):trane baystat 239 to honeywell rth230 H" , posted Sun 25 May 16:55:  
If you choose the RTH7400 or RTH7500...
Option 170 = 7 option 190 = 0 Your old B is C (common) Tape off your tan wire.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Sun 25 May 20:05] |
|
|