| makertoutle | "Intertherm electric Furnace problem" , posted Tue 27 May 17:01  
I have an Intertherm Electric Furnace model # E2EH-020HB. One half of the lower heating coil is staying on and the fan is running contantly at a lower pseed, which is not normal. The heating coils look fine, no burning or melting found, no cross grounding found. I disconecting the power to the coil that is staying on, it is now off but the fan is still running. I disconected the sequencer to the coil, but it stilol stayed on. What could be the issue?
Mark
| | Replies:
|
| makertoutle | "Re(1):Intertherm electric Furnace problem" , posted Tue 27 May 18:01  
Problem cured. Pulled out the heating coils units (2), discovered one coil pastialy touching the coil assembly frame causing a ground draw. bent coil away from the frame, re-assembled, all works great...
Mark
|
|
|