| Banger 
| "Re(1):Honeywell round to LUX TX500 Thermostat" , posted Sat 31 May 08:39  
The Lux and the honeywell both use the same terminal identifiers so you should be able to look at where the old wires were and match them up to the new thermostat terminals. If the wire came from the Y terminal, put it back on the Y terminal, etc. Be careful you don't mix up the 2 R terminals, Rh is for heat and Rc is for cool. Your system may have them seperated if you have hot water heat.
|
|
|