I have a Goodman A36-15 Air Handler/Heater. The A/C unit outdoors kicks on and everything is working except the Blower fan is on low setting. It does not push the air through the vents. You can only feel low pressure but air is cold. Also causing a lot of condensation on the coils, which caused a blocked drain pipe and leak.

Any ideas on how I can fix this?

 


Replies:

Houston204



98.196.66.53

"Re(1):Goodman A36-15 Blower Problem" , posted Wed 6 Aug 01:09:user profileedit/delete messagepost reply


I believe the 3 ton unit comes factory wired for high speedbut this is not hard to verify. If black from your motor is capped off, you are using low speed, if red is capped off you are using high speed. (See note 1)





It is also possible that the evaporator coil is dirty or the cap is weak.

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Wed 6 Aug 01:10]

 

 

DFS

71.11.170.11

"Re(2):Goodman A36-15 Blower Problem" , posted Wed 6 Aug 13:02user profileedit/delete messagepost reply


Thanks for the diagram. The red is capped off. After I posted I took the unit apart to see if I could increase the speed of the motor. I found that the lines were frozen. I let it thaw and it seems to be blowing alot colder and stronger.

The unit had to run from 94F to 80F overnight so I don't know if this is what caused it to freeze or not. Maybe low on Freon??

Thanks for the help.