Good Morning All ..I have a Rudd UPNE-036JAZ Heatpump 3 ton that I been working on..the unit keeps tripping on low pressure cut out..checked pressures running very low 35/155..I know you all are going to say a leak...there is no leak..the RV wasnt energized in cooling so I switched the setting in the stat and it did energize but pressures went to what you would expect from heat mode so I switched back. No matter how much gas you add the pressure never seems to raise?????

 


Replies:

sinead26ohara

24.160.212.197

"Re(1):Rudd 3 ton HP NEED SOME HELP HERE" , posted Sun 31 Aug 23:37user profileedit/delete messagepost reply


You could have a RV hanging up.

Sinead O'Hara

 

coolboy

74.167.117.9

"Re(1):Rudd 3 ton HP NEED SOME HELP HERE" , posted Wed 20 Aug 19:39user profileedit/delete messagepost reply


Compressor valves are shot. Replace compressor or unit.

If the work aint tight it aint right!

 

 

theduke03

24.250.18.179

"Re(2):Rudd 3 ton HP NEED SOME HELP HERE" , posted Wed 20 Aug 20:08user profileedit/delete messagepost reply


How could the unit trip on low pressure if the compressor valves are shot? I suppose this could be true if the system was empty and has bad valves but; if it was empty you wouldn't be able to verify the bad valves theory.

"My dad was the most feared furnace fighter in Northern Indiana."

 

theduke03

24.250.18.179

"Re(1):Rudd 3 ton HP NEED SOME HELP HERE" , posted Wed 13 Aug 08:59user profileedit/delete messagepost reply


I'm not sure what you're saying about the revertsing valve but get it running in a/c mode. Measure the following and post results.
suction pressure
head pressure
suction line temp
liquid line temp
outdoor ambient temp
TXV or orifice?