Original message
| EEAir | "Carrier Fa4anf036 will not cool" , posted Tue 19 Aug 21:36  
We have a carrier split system model # Fa4an036-38ycc036-3. It will not cool. It is only blowing hot air. We have made no changes. It was just working one day and stopped the next. It has been working for over 7 years with no problems. Any suggestions?
Thank you Ben
| | Replies:
|
| coolboy | "Re(1):Carrier Fa4anf036 will not cool" , posted Wed 20 Aug 19:47  
You need to post more info. Is the outside fan spinning? Is the compressor humming?
If the work aint tight it aint right!
|
| Jojo98 | "Re(1):Carrier Fa4anf036 will not cool" , posted Tue 19 Aug 22:06  
Turn the circuit breaker off for the outdoor unit. Wash the outdoor coil with water. Change the air filter. Reset the circuit breaker to ON, verify that the t-stat is calling for cooling. If the A/C starts cooling, might have been dirty; call a service company and have them service the A/C. If the outdoor unit doesn't start ( compressor and condenser fan ) cal a service company.
|
|
|