Carrier Fa4anf036 will not cool - http://www.hvacmechanic.com/ Forums


Original message

EEAir

24.170.144.17

"Carrier Fa4anf036 will not cool" , posted Tue 19 Aug 21:36user profileedit/delete messagepost reply


We have a carrier split system model # Fa4an036-38ycc036-3. It will not cool. It is only blowing hot air. We have made no changes. It was just working one day and stopped the next. It has been working for over 7 years with no problems. Any suggestions?

Thank you
Ben

 


Replies:

coolboy

74.167.117.9

"Re(1):Carrier Fa4anf036 will not cool" , posted Wed 20 Aug 19:47user profileedit/delete messagepost reply


You need to post more info. Is the outside fan spinning? Is the compressor humming?

If the work aint tight it aint right!

 

Jojo98

68.60.207.210

"Re(1):Carrier Fa4anf036 will not cool" , posted Tue 19 Aug 22:06user profileedit/delete messagepost reply


Turn the circuit breaker off for the outdoor unit. Wash the outdoor coil with water. Change the air filter. Reset the circuit breaker to ON, verify that the t-stat is calling for cooling. If the A/C starts cooling, might have been dirty; call a service company and have them service the A/C. If the outdoor unit doesn't start ( compressor and condenser fan ) cal a service company.