"Non-Condensables?" , posted Mon 25 Aug 22:45user profileedit/delete messagepost reply


I've been working on a 5 ton R-22 trane system with a txv metering device.The evap coil has been freezing up,suction pressure obviously low,head pressure was ok,subcooling dead on.I changed the txv,now same thing.I've even raised the fan speed from medium to high,still freezing.I'm racking my brain here,could it be non-condensables? Or am I missing something here?

 


Replies:

sinead26ohara

24.160.212.197

"Re(1):Non-Condensables?" , posted Wed 3 Sep 20:30user profileedit/delete messagepost reply


How is your return air? Is it possible that a blockage has occured in the return air duct?

Sinead O'Hara

 

Silvertop



97.82.169.41

"Re(1):Non-Condensables?" , posted Wed 27 Aug 06:52user profileedit/delete messagepost reply


Try this site, it will tell you how to troubleshoot a TXV

http://www.virginiaair.com/formbox/Solutions%20for%20Fixing%20Common%20TXV%20Problems.pdf

One step at a time

 

Jojo98

68.60.207.210

"Re(1):Non-Condensables?" , posted Tue 26 Aug 22:35:user profileedit/delete messagepost reply


Non-condensibles elevate head pressure. Outdoor air temp dictates head pressure, OAT + 30deg is a good rule of thumb. Did you weigh in the charge. A searching TXV: Check location of TXV bulb (4-5 or 8-9 o'clock) ensure entire bulb fits tightly against suction line, and is insulated. Make certain bulb is several inches downstream of ext. equalization line. If you previosly posted about mismatching SEER rated coils, then you are going to have issues. Let me know I have some data that could be helpful.

[this message was edited by Jojo98 on Tue 26 Aug 22:46]

 

Silvertop



97.82.169.41

"Re(1):Non-Condensables?" , posted Tue 26 Aug 07:38user profileedit/delete messagepost reply


If you have the numbers, you need to post them. What is the super heat, discharge and suction pressure, etc..

One step at a time

 

amech

68.79.171.167

"Re(1):Non-Condensables?" , posted Tue 26 Aug 06:07user profileedit/delete messagepost reply


I read nothing about changing out the drier. Did you?

 

 

green1982

69.148.72.196

"Re(2):Non-Condensables?" , posted Tue 26 Aug 18:00user profileedit/delete messagepost reply


No I didn't change the filter dryer.I didn't notice until after I started it up again that trane has the filter dryer installed in the condensor.But my head presssure is about 200,suction is fluctuating from 10 to 50 psi.Very strange.

 

 

Trane gang

75.213.76.199

"Re(3):Non-Condensables?" , posted Tue 2 Sep 16:46:user profileedit/delete messagepost reply


Definetly not non-condensables!!!!!
It sounds more like you have a restriction in your piping. What is your subcooling? what is your superheat? Trane like to stick with 10-15 degree superheat. and a subcooling of about 30 degrees.
Could be a dirty evap coil of a lack of airflow.

[this message was edited by Trane gang on Tue 2 Sep 16:48]