| kyle987 | "ac blows but does not cool" , posted Mon 1 Sep 09:48  
my ac blows but will not cool. after reading through all the helpfull tips i thought i would give you guys a whirl. i tried listening for a hum while the outsid unit is running and I can hear the compressor hum shortly every 10 seconds or so. please help! thanks
| | Replies:
|
| Jojo98 | "Re(1):ac blows but does not cool" , posted Mon 1 Sep 23:07  
I'm willing to bet the A/C doesn't have a start capacitor. If you have a clamp-on ammeter, attach the meter to the common leg of power, usually black wire to the compressor, and comming from the contactor. Read the amp draw at start-up, and compare the reading to the unit data plate. You are measuring LRA; lock rotor amps, the ammount of current the compressor pulls when the compressor is locked up, and must be replaced. If you don't have a meter, then call a service company.
|
| rlj1117 | "Re(1):ac blows but does not cool" , posted Mon 1 Sep 10:16  
sounds like start capacitor
|
|
|