my ac blows but will not cool. after reading through all the helpfull tips i thought i would give you guys a whirl. i tried listening for a hum while the outsid unit is running and I can hear the compressor hum shortly every 10 seconds or so. please help! thanks

 


Replies:

Jojo98

68.60.207.210

"Re(1):ac blows but does not cool" , posted Mon 1 Sep 23:07user profileedit/delete messagepost reply


I'm willing to bet the A/C doesn't have a start capacitor. If you have a clamp-on ammeter, attach the meter to the common leg of power, usually black wire to the compressor, and comming from the contactor. Read the amp draw at start-up, and compare the reading to the unit data plate. You are measuring LRA; lock rotor amps, the ammount of current the compressor pulls when the compressor is locked up, and must be replaced. If you don't have a meter, then call a service company.

 

rlj1117

24.181.246.138

"Re(1):ac blows but does not cool" , posted Mon 1 Sep 10:16user profileedit/delete messagepost reply


sounds like start capacitor