"SV9541 Smart Valve" , posted Tue 30 Sep 17:31user profileedit/delete messagepost reply


I have 3 year old tempstar furnace, model 8mpn, nat gas. The thing fires up whith tstat locked high, vent fan comes on, pilot lites, burner will not light. It trys this a couple times and then shuts down for a few minutes and then trys again. It has a honeywell sv9541 valve, it blinks green 6+1. I am not getting a call for main gas or the main gas valve is not opening. Vacuum switch is closing, everything seems fine, just no main gas. Any ideas? Could the gas valve be bad? How could I check that?

Jay

 


Replies:

GRYNCHROCK

138.230.48.18

"Re(1):SV9541 Smart Valve" , posted Thu 16 Oct 16:31:user profileedit/delete messagepost reply


Bad valve, replaced valve, works just fine now.

Jay

[this message was edited by GRYNCHROCK on Thu 16 Oct 16:32]

 

tom446



66.66.203.58

"Re(1):SV9541 Smart Valve" , posted Tue 30 Sep 19:52user profileedit/delete messagepost reply


The pilot may not be proving itself. Try removing the ignitor and clean the flame sense rod with a piece of steelwool. Be careful to stay away from the ignitor with the steel wool.

If in doubt call a pro !

 

 

grynchrock

138.230.48.18

"Re(2):SV9541 Smart Valve" , posted Thu 2 Oct 08:13:user profileedit/delete messagepost reply


Thanks for the input! Also, thanks for the troubleshooting guide! The exhaust fan kicks on and the pressure switch is closing so I have enough vacuum. I had broken the pilot assembly while trying to clean it, I replaced it with new and the new one works well. I did take a mvolt reading while the pilot was lighting and with no pilot I read 0 mvolts, when the ignitor comes on I instantly get an increasing signal all the way up to 400 mvolts when the pilot flame is burning. So it looks like the pilot and thermocouple are working. Going by the troubleshooting guide that was attached above, I need to check my gas pressure. What range of gas pressure should I see for correct operation?

Jay

[this message was edited by grynchrock on Thu 2 Oct 08:14]

 

 

Schock Therapy

75.157.133.30

"Re(2):SV9541 Smart Valve" , posted Tue 30 Sep 21:00:user profileedit/delete messagepost reply


I'll second that! It definitely sounds like a flame proving problem. make sure the flame rod, and ground rod are clean, the ceramic is not cracked. also make sure that the pilot flame is making good contact with the two flame rods. If it still doesnt work, change the flame rod.

It's only a shock if your not expecting it!

[this message was edited by Schock Therapy on Tue 30 Sep 21:06]

 

 

Houston204



98.196.66.53

"Re(3):SV9541 Smart Valve" , posted Wed 1 Oct 23:19user profileedit/delete messagepost reply


I agree.