Original message
| t1551fo | "Armstrong ultra 90" , posted Thu 2 Oct 20:08  
Had problum with ignitor,replaced it with new unit, pilot comes on heats up probe, small blower and main blower come on no main burners what can i check next all conneection on circuit board look good
18892
| | Replies:
|
| Jojo98 | "Re(1):Armstrong ultra 90" , posted Fri 3 Oct 20:08  
If your safeties are closed, then check to see if you are getting 24v to the main gas valve. Call for a demand for heat, and listen for a click noise coming from the MGV, thats the solenoid energizing and allowing gas to flow.
|
|
|