Hi, My furnace wouldn't start when I tried to fire it up for the first time this year. The fan comes on to start the draft for about 15 secs, then the igniter comes on, then nothing ignites and the furnace shuts down and has to be reset. The led light shows no error codes. Any help would would be appreciated.
Thanks

 


Replies:

amech

68.249.110.53

"Re(1):Janitrol furace problems" , posted Sun 5 Oct 09:36user profileedit/delete messagepost reply


Maybe a bad gas valve or limit switch. Do you own a volt meter. If you do, check for 24V at the gas valve and across limits.

Hope this helps

 

 

ronrobbie7

75.39.224.124

"Re(2):Janitrol furace problems" , posted Sun 5 Oct 12:05user profileedit/delete messagepost reply


Going to buy meter today. Thanks for the help. Do you know what settings to have the meter on when testing? I know there are alot of settings on some of them.