Original message
| siestavista | "overfireing furnace" , posted Wed 8 Oct 13:06  
an old sears furnace has been retrofited with a new gas valve and standing pilot where an old spark ignightor existed. it has a 42 oriface. It has not been deregulated for altitude. at 4,600'and a specific gravity of 1000 btu for the natural gas 80% of 75,000btu input rating= 60,000. if you look on the chart it will read an oriface size of (i'm guessing here) 38. am i in the ball park?
| | Replies:
|
| siestavista | "Re(1):overfireing furnace" , posted Fri 10 Oct 20:35  
HIGH ALTITUDE INSTALLATION INSTRUCTIONS For HA02 Conversion Kit Nat. & L.P. Gases IMPORTANT NOTICE This conversion kit is to convert the gas furnace for higher altitudes. These instructions are intended for the use of qualified individuals who are trained and experienced in the installation and conversion of this type of equipment. Personnel performing this task are required in some states to be licensed. Under no circumstances should this conversion, or equipment installation be performed by personnel who are not qualified. Failure to observe this warning may result in equipment damage, fire, or life threatening danger. Refer to the equipment installation manual, the National Fuel Gas Code (ANSI Z223.1), or in Canada (CAN/CGA1-2.17-M91), and local codes. PARTS LIST Using the following parts list, ensure that all parts included in this list are present and in an undamaged condition. WARNING IF ANY DOUBT EXISTS ABOUT THE CONDITION OF ANY COMPONENT WITHIN THIS KIT, DO NOT USE THIS KIT AND CONTACT YOUR SUPPLIER FOR A NEW KIT. DESCRIPTION PART NUMBER QUANTITY Installation Instructions IO-552 1 Conversion Label B14933-63 1 Burner Orifices B25899-01 thru -10 6 ea./pack PARTS LIST TOOLS REQUIRED FOR INSTALLATION (2) Pipe Wrenches. These wrenches shall be suitably sized to handle the supply piping and its ground joint union. (1) 7/16 open or closed wrench. Do not use an adjustable wrench when removing or installing burner orifices. (1) 5/16 nut driver. (1) Flat blade screw driver. All information contained herein is subject to change without notice. Goodman Manufacturing Company, L.P. I0-552A 2550 North Loop West, Suite 400, Houston, TX 77092 08/04 www.goodmanmfg.com © 2004 Goodman Manufacturing Company, L.P. (1) 3/16 Allen wrench. The Allen wrench is required to remove gas valve inlet and outlet plugs. (2) Water Column manometers. Manometers are to be capable of reading a range between 0 and 20 inches with 1" increments. Pipe thread compound. Pipe thread compound used must be listed as appropriate material for LP gas. Soap solution and application brush. IO-552A 2 08/04 INSTALLATION WARNING NEVER USE AN OPEN FLAME WHEN CHECKING FOR GAS LEAKS. USING AN OPEN FLAME COULD RESULT IN FIRE, CAUSING PROPERTY DAMAGE, PERSONAL INJURY OR DEATH. WARNING TURN OFF ELECTRICAL POWER AND GAS SUPPLY TO THE APPLIANCE. 1. Prior to performing this conversion, refer to the Installation & Operation Manual supplied with the unit, the National Fuel Gas Code (ANSI Z223.1) or in Canada CAN/CGA1- 2.17-M91), and local codes to ensure that this appliance is installed correctly and in compliance with these codes/ manuals. 2. Set the room thermostat to its lowest possible setting. 3. Remove the furnace control access door. See figure 1 for the location of these components. 4. Loosen the gas supply ground union, and remove the gas valve supply line. Use one pipe wrench as a back-up to prevent damage/rotation of any controls. 5. Remove the (4) sheet metal screws which fasten the gas manifold to the burner box. See figure 1. for component location. On PGB series take care not to break the Hot Surface Ignitor on the pilot assembly. 6. Using the 7/16 wrench, remove the existing natural gas orifices from the burner manifold. Discard the natural gas orifices. 7. Install the orifices supplied with this kit into the gas manifold. Look at sizes stamped on orifice face to insure that all the same are installed. Tighten these orifices adequately to prevent gas leakage. Refer to table 1 for the correct burner orifices. 8. Using the 3/16 Allen wrench, remove both the gas valve inlet and outlet pressure plugs. Retain these plugs. 9. Install a barb hose connector into both the gas valve inlet and outlet pressure ports. Note: The gas valve pressure ports are threaded to accept a 1/8 NPT fitting. Do not use a barbed hose connector that is threaded for anything other than 1/8 NPT. 10. Reinstall gas manifold assembly into furnace. 11. Connect both the inlet and outlet gas valve barb fittings (installed in step 9) to (2) separate manometers. See figure 2. 12. Apply a liberal quantity of pipe thread compound to all threaded portions of the gas supply piping. Pipe compound must be resistant to the effects of LP gas. 13. Install the gas supply piping and its ground union joint using a pipe wrench. Use a second pipe wrench as a back up. WARNING DO NOT USE AN OPEN FLAME TO CHECK THE GAS SUPPLY LINE, GAS VALVE INLET AND OUTLET PRESSURE AREAS. 14. Turn on the gas supply to the furnace. Using a soap and water solution, check the gas supply line, gas valve inlet and outlet pressure areas. Repair any gas leaks detected. 15. Turn on the electric supply to the furnace. 16. Adjust the room thermostat to obtain continuous burner operation. 17. After the burner is in operation for 15 minutes, check and adjust, if needed , the supply and manifold pressure. See figure 2. 18. Adjust the burner air shutters to obtain a burner flame consistent with the flame shown in the furnace Installation & Operating Instructions. 19. Turn off the gas and electrical supply to the furnace. 20. Apply the conversion label adjacent to the rating plate. 21. Remove the barb fittings and manometers installed on the gas valve. Install the gas valve inlet and outlet pressure plugs. 22. Turn on the gas and electrical supply. Adjust the room thermostat to ensure continuous burner operation. WARNING DO NOT USE AN OPEN FLAME TO CHECK THE GAS SUPPLY LINE, GAS VALVE INLET AND OUTLET PRESSURE AREAS, AND THREADED PORTIONS OF THE BURNER ORIFICES FOR LEAKS. 23. Using a soap solution check the gas supply, gas valve inlet and outlet pressure areas, and threaded portions of the burner orifices for leaks. Repair any gas leaks detected. 24. Observe at least three ignition cycles to ensure smooth and quiet ignition. 25. Install the control access panel. IO-552A 3 08/04 BURNER MANIFOLD BURNER BOX GAS VALVE ACCESS DOOR FIGURE 1 Note: Typical Up-flow Furnace. Actual Models May Differ. GAS FLOW INLET (SUPPLY) PRESSURE MANOMETER (FIELD SUPPLIED) NOTE! SUPPLY PRESSURE IS TO BE BETWEEN 5.0 & 7.0 NAT AND 11.0 & 14.0 L.P. INCHES WITH THE FURNACE OPERATING. INLET (SUPPLY) PRESSURE HOSE FITTING (FIELD SUPPLIED) OUTLET (MANIFOLD) PRESSURE HOSE FITTING (FIELD SUPPLIED) OUTLET (MANIFOLD) PRESSURE MANOMETER (FIELD SUPPLIED) NOTE! MANIFOLD PRESSURE IS TO BE BETWEEN 3.2 & 3.7 NAT AND 10.0 & 11.0 L.P. INCHES. FIGURE 2 IO-552A 4 08/04 Table 1, 2 and 3 are based upon the furnace input being reduced for altitudes above sea level. U.S. 4% per 1000 feet. Canada 10% derate for 2000-4500 feet. To determine input/burner, locate input rate on plate and divide by number of burners. If specific input/burner is not listed, use the values of the next lower table (i.e. If input/burner is 24,500, use the values in Table1, if input/burner is 21, 800, use Table 3, etc.). INPUT/BURNER 2000 3000 4000 4500 5000 6000 7000 8000 U.S. BURNER ORIFICE 44/55 44/55 45/56 45/56 46/57 47/58 47/58 CANADA BURNER ORIFICE 44/55 47/57 INPUT/BURNER 2000 3000 4000 4500 5000 6000 7000 8000 U.S. BURNER ORIFICE 43/55 53/55 44/56 44/56 44/56 45/57 45/57 CANADA BURNER ORIFICE 43/55 46/57 INPUT/BURNER 2000 3000 4000 4500 5000 6000 7000 8000 U.S. BURNER ORIFICE 45/55 47/55 47/56 47/56 48/57 48/58 49/58 CANADA BURNER ORIFICE 45/55 48/57 20,000 BTUH NAT/20,OOO BTUH/L.P. ELEVATION ABOVE SEA-LEVEL (FEET) TABLE 1 TABLE 2 TABLE 3 22,500 BTUH NAT/20,OOO BTUH/L.P. ELEVATION ABOVE SEA-LEVEL (FEET) 25,000 BTUH NAT/20,OOO BTUH/L.P. ELEVATION ABOVE SEA-LEVEL (FEET) Quality Makes the Difference! All of our systems are designed and manufactured with the same high quality standards regardless of size or efficiency. We have designed these units to significantly reduce the most frequent causes of product failure. They are simple to service and forgiving to operate. We use quality materials and components. Finally, every unit is run tested before it leaves the factory. Thats why we know. . . Theres No Better Quality. Visit our web site at www.goodmanmfg.com for information on: Goodman products Warranties Customer Services Parts Contractor Programs and Training Financing Options © 2004 Goodman Manufacturing Company, L.P.
|
|
|