Will turn on w/o blower for a few secs, doesn't ever go entirely on. Is blinking 3 times (Pressure switch open with inducer on). What the heck does that mean? Something I can do or should I just call the specialist? We installed it ourselves so we have some knowledge.
| | Replies:
|
| acefurnacefxr 
| "Re(1):New Lennox, worked great 1st day, now o" , posted Mon 20 Oct 14:59  
DONT CHECK NOTHING.............DO NOT TOUCH THE UNIT .............CALL THE INSTALLING CONTRACTOR AND HAVE THEM FIX IT.
HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT
I have been performing HVAC repairs for 23 years
http://www.barackobama.com
|
| | Schock Therapy | "Re(2):New Lennox, worked great 1st day, now o" , posted Mon 20 Oct 22:27:  
Read the post more carefully acefurnacefxr, they installed the furnace themselves. You and I both know that it is likely a very simple fix. It doesn't take 23 years experience to reconnect a pressure switch tube. If you don't like the fact that a homeowner has installed his own furnace, talk to Lennox...they sold it to him!
It's only a shock if your not expecting it!
[this message was edited by Schock Therapy on Mon 20 Oct 22:30] |
| Schock Therapy | "Re(1):New Lennox, worked great 1st day, now o" , posted Sun 19 Oct 17:36  
Check that the rubber tube is connected from the inducer fan housing to the pressure switch. Make sure the electrical connections on the pressure switch are good.
It's only a shock if your not expecting it!
|
|
|