| RobertR | "Re(1):Trane thermostat no power" , posted Fri 24 Oct 23:48  
Retired Mechanical Design Engineer that worked as an HVAC/R mechanic to pay for his education.
|
| RobertR | "Re(1):Trane thermostat no power" , posted Wed 22 Oct 16:22  
Retired Mechanical Design Engineer that worked as an HVAC/R mechanic to pay for his education.
|
| RobertR | "Re(1):Trane thermostat no power" , posted Mon 20 Oct 18:14:  
You have lost control voltage (24v a/c). The most likely candidates are usually all next to each other inside the indoor unit (AHU)on Trane. You have: 1. a blown control fuse (look for a black plastic holder near the control transformer with two wires going to it or they sometimes mount the fuse holder right on the transformer. OR
2. a popped control voltage circuit breaker (look for a round black plastic piece approximately 3/4" in diameter with a red or white push-button ticking out of it and press the button in the center one time only - if it does not reset you need a technician. AND/OR
3. you have a bad control transformer - for this you should have a technician check why the transformer failed.
Retired Mechanical Design Engineer that worked as an HVAC/R mechanic to pay for his education.
[this message was edited by RobertR on Mon 20 Oct 18:29] |
|
|