| eorb99 | "BAY28X139 to Hunter 44860" , posted Wed 22 Oct 20:55  
I have the BAY28X139 but I'm trying to go to a Hunter 44860. This is the configuration I have found on the web. Is this correct?
W = W2 X2 = E B = C G = G O = O Y = Y1 R = R T = Goes to nothing
| | Replies:
|
| Zzz | "Re(1):BAY28X139 to Hunter 44860" , posted Thu 23 Oct 23:44  
before you go to far bring that hunter back and buy a honeywell.
|
| | eorb99 | "Re(2):BAY28X139 to Hunter 44860" , posted Fri 24 Oct 14:10  
No store around me carries the one I need.
|
| | Houston204 
| "Re(3):BAY28X139 to Hunter 44860" , posted Sat 25 Oct 01:32  
I would use a Honeywell that is available over a Hunter stat. I agree with your wiring though. You must also configure your new stat for heatpump operation as described on pages 28 and 29 of your manual.