"BAY28X139 to Hunter 44860" , posted Wed 22 Oct 20:55user profileedit/delete messagepost reply


I have the BAY28X139 but I'm trying to go to a Hunter 44860. This is the configuration I have found on the web. Is this correct?

W = W2
X2 = E
B = C
G = G
O = O
Y = Y1
R = R
T = Goes to nothing

 


Replies:

Zzz

64.59.144.21

"Re(1):BAY28X139 to Hunter 44860" , posted Thu 23 Oct 23:44user profileedit/delete messagepost reply


before you go to far bring that hunter back and buy a honeywell.

 

 

eorb99

68.49.187.168

"Re(2):BAY28X139 to Hunter 44860" , posted Fri 24 Oct 14:10user profileedit/delete messagepost reply


No store around me carries the one I need.

 

 

Houston204



98.196.66.53

"Re(3):BAY28X139 to Hunter 44860" , posted Sat 25 Oct 01:32user profileedit/delete messagepost reply


I would use a Honeywell that is available over a Hunter stat.
I agree with your wiring though. You must also configure your new stat for heatpump operation as described on pages 28 and 29 of your manual.