Original message
| coalfarmer | "coleman evcon blower will not come on" , posted Fri 24 Oct 12:11  
I have a Coleman Evcon model DGATO75BDC 14 years old.. In the past 3 years i have replaced 2 igniter bars 1 blower motor and last year a fan switch...This year on my first start up of the season it acted like the fan switch was out again,but 14 dollars later and a new fan switch the unit is still not working..After a few phone calls i was told to check the fan relay, this unit has 3 relays and from what i can see 2 snap in when power is turned on the furnace and the other only comes in when the unit is turned to AC mode.. The relays snap in hard and have no chatter like a weak coil and the blower works in the AC mode.. On start up glow bar comes on, burner lights and stays lit for about 2 minutes just about the time the blower should come on the unit shuts down and if i let it try to start up a second time it pops the thermal breaker from overheating.. This is a bare bones unit no flashing board lights like some coleman evcon units... So if anyone has had the problem and can share some info it would sure help.. thanks Steve
save a buck and do it yourself