York Stellar Plus won’t ignite

Natural gas furnace, 12 years old, small, only heats 2 rooms, photo with upper part door open here:

http://members.cox.net/obryskin/image/P1020401.jpg

Sticker says model # M3UF024SA, can’t find it anywhere.

Situation:
When heat is switched on motor starts running, pressure switch (the one on the right with 2 wires) closes (multimeter reads 0V), but hot surface igniter won’t ignite.
Disconnected the igniter and there is no voltage coming in to igniter contacts.
Igniter itself looks OK, not broken, a little charred, ordered new one just in case.
No diagnostic LED here, like our other unit York Diamond 80 has.

Question:
What could be the problem, can I test further myself or call a pro?

 


Replies:

jayman

75.66.2.89

"Re(1):York Stellar Plus won’t ignite" , posted Sat 1 Nov 09:23user profileedit/delete messagepost reply


unable to see image but try control board

jason m&m

 

 

purcki

68.98.163.153

"Re(2):York Stellar Plus won’t ignite" , posted Sat 1 Nov 11:07user profileedit/delete messagepost reply


Here is the picture
Where is this control board and how to test it?

 

 

jayman

75.66.2.89

"Re(3):York Stellar Plus won’t ignite" , posted Sat 1 Nov 19:38user profileedit/delete messagepost reply


couple of things first is that a second pressure switch and has it been checked. second check in the blowwer housing for the control board. I see wires running to the bottem of the unit.try that and let me know

jason m&m

 

 

purcki

68.98.163.153

"Re(4):York Stellar Plus won’t ignite" , posted Tue 4 Nov 11:13user profileedit/delete messagepost reply


Found answer to the problem on another forum, thermal switch(fuse) was bad. Waiting for the part now.