"Connecting HE360 to furnace" , posted Tue 4 Nov 17:11user profileedit/delete messagepost reply


Can a Honeywell HE360 humidifier and humistat be attached directly to a gas furnace?

I have two yellow wires from the humidifier and 2 black wires from the humidistat and need know how to wire to the furnace. I would like the HE360 to turn on when the furnace blower turns on.

bobk

 


Replies:

Houston204



98.196.66.53

"Re(1):Connecting HE360 to furnace" , posted Tue 4 Nov 21:05user profileedit/delete messagepost reply


You can energize the 24VAC coil of a relay closing a set of normally open contacts using the Hum terminal and C. (If furnace has a Hum terminal)

If you do not have an H terminal, I recommend a current sensing relay. I do not like sail switches.




"Tip of the Day" Remember to remove power first.

 

 

bobkcolo

128.221.197.21

"Re(2):Connecting HE360 to furnace" , posted Wed 5 Nov 10:50user profileedit/delete messagepost reply


Thanks for the prompt reply.

The furnace circuit board has 5 screw connectors (G, W, C, Y, R) labeled 'thermostat'. Tab style connectors have wires that go to the furrnace internals and a Honeywell S8610u (ignitor?). I did not notice a connector labeled 'HUM'.

Sounds like the curent sensing relay is how I should proceed. Where would the relay be connected?

bobk

 

 

Houston204



98.196.66.53

"Re(3):Connecting HE360 to furnace" , posted Wed 5 Nov 19:43user profileedit/delete messagepost reply


Your blower common wire runs through it as shown in the diagram.

"Tip of the Day" Remember to remove power first.