| RookieItSelf | "Home Thermostat installation - wiring confusi" , posted Mon 10 Nov 18:17  
Replacing an old Honeywell with a Hunter Model 44660. The old unit has 5-wires. On the back of the Honeywell the wire color and connections were: White wire to the "W" connection; Red wire to the "R" connection; Yellow wire to the "Y" connection; Blue wire and green wire together connected to the "G" connection.
I have an auto fan and cooling working on cue at an appropriate setting. No heat.
Current wire connection on the Hunter Model 44660:
G port has green wire; W/B Port has White & Blue wire Y/G port is empty; RC port has Red wire RC1 is empty; RH is empty; Y1 has yellow wire.
What is mixed up and will bring heat? Many thanks.
Rookie (Does it show??)
RookieItSelf
| | Replies:
|
| wingnut_2u | "Re(1):Home Thermostat installation - wiring c" , posted Tue 11 Nov 04:17:  
hook the wires as follows.
wire--------thermostat red -------- RC1 white ------ W/B yellow ----- Y/O blue/green-- G Jumper RC and RH System Selector switch to HG/HE
TURN POWER OFF FIRST!
[this message was edited by wingnut_2u on Tue 11 Nov 04:27] |
| | Houston204 
| "Re(2):Home Thermostat installation - wiring c" , posted Wed 12 Nov 08:10  
You will also need to jumper Rc to R1.
"Tip of the Day" Remember to remove power first.
|
| mississippi | "Re(1):Home Thermostat installation - wiring c" , posted Mon 10 Nov 20:48  
You need a jumper between RC and RH.
|
| | Houston204 
| "Re(2):Home Thermostat installation - wiring c" , posted Mon 10 Nov 21:00:  
Use the lower diagram.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Mon 10 Nov 21:00] |
|
|