| | Preview | User | Replies | |
 | "Ran centrak home AC with cover " , posted Sat 7 Jun 22:40
HiMy wife flipped on the AC last night for first time this year. The cover was on and it was running this way for several hours before I got home and removed the cover. It was very hot. The ... read more |
moenlou
 |
Replies (3) Re(1):Ran centrak home AC with cover - moenlou Re(1):Ran centrak home AC with cover - yuri Re(2):Ran centrak home AC with cover - tinner73
| |
 | "AC compressor not cutting off- ColemanEvcon " , posted Sat 7 Jun 18:20
After an electical storm, my out side unit will not cut off. Compressor and pipes freeze up. Why? Thanks, MLB1. ... read more |
mlb1
 |
Replies (6) Re(1):AC compressor not cutting off- ColemanE - mlb1 Re(2):AC compressor not cutting off- ColemanE - Houston204 Re(3):AC compressor not cutting off- ColemanE - mlb1 Re(1):AC compressor not cutting off- ColemanE - tinmantu Re(1):AC compressor not cutting off- ColemanE - mlb1 read more
| |
 | "Sears model 867.762230 " , posted Sat 7 Jun 16:55
I have an 8 year old, never installed, Sears model 867.762230 natural gas furnace, needing conversion kit to propane, or LP. After some searching, I think the real maker may be Tempstar, which is real ... read more |
leehinkleman
 |
Replies (2) Re(1):Sears model 867.762230 - Houston204 Re(2):Sears model 867.762230 - leehinkleman
| |
 | "hard start wiring ???? " , posted Sat 7 Jun 07:08
Can someone help with the wiring of a hardstart kit. Haven't done one in a long time. Going on a 1990 Model Trane XL1200 5 ton heatpump ... read more |
kaj58
 |
Replies (3) Re(1):hard start wiring ???? - theduke03 Re(2):hard start wiring ???? - kaj58 Re(3):hard start wiring ???? - Houston204
| |
 | "a/c " , posted Fri 6 Jun 23:52
i just had a a/c unit installed. it comes on and runs to the set temp and turns off. when the temp rises the fan comes on but not the commpressor. i changed the tstat and still same issue. do i have t ... read more |
crna2011
 |
Replies (1) Re(1):a/c - theduke03
| |
 | "Carrier fb4anf036 coil replacement " , posted Fri 6 Jun 19:27
Hello, I have a Carrier unit model fb4anf036 and I've been told that the coil is really beyond cleaning and that I need to replace the whole thing to a goodman 3ton. I really don't have the money to r ... read more |
pepeofaustin
 |
Replies (1) Re(1):Carrier fb4anf036 coil replacement - theduke03
| |
 | "need some education " , posted Fri 6 Jun 13:24
Whats the best online school for HVAC maintnance and repair. ... read more |
stepkajam
 |
Replies (1) Re(1):need some education - Technician
| |
 | "unit frost in winter and not working in summe " , posted Fri 6 Jun 12:27
I have an arcoaire powermax10. In the winter there was about 1" of frost on the outside and inside. In the summer the unit comes on but the air is not cool and is barely coming out of the vents. Wh ... read more |
micondy
 |
Replies (2) Re(1):unit frost in winter and not working in - Frostline Re(1):unit frost in winter and not working in - yuri
| |
 | "Compressor chatter before start up " , posted Fri 6 Jun 08:48
I have a 10 SEER scroll compressor that makes a noise like a contactor chattering inside the compressor berfore it runs.Once started it works great.Checked capacitor-35-3 Reads 33.4 and 3.3 mf.Any ide ... read more |
frostline
 |
Replies (16) Äîáðûé äåíü! Excel VBA - vbahelp Äîñòàâêà öâåòîâ â Ìèíñêå è Áåëàðóñè - abelflower Ñêà÷àé ÏÎÐÍÎ ÂÈÄÅÎ! ÁÅÑÏËÀÒÍÎ!!! - aresearchandmarkets Âàó! Ñêà÷àé ÏÎÐÍÎ ÂÈÄÅÎ! ÁÅÑÏËÀÒÍÎ - aresearchandmarkets Âàó!!! Ñêà÷àé ÏÎÐÍÎ ÂÈÄÅÎ! ÁÅÑÏËÀÒÍÎ - aresearchandmarkets read more
| |
 | "13 yr old Trane Outdoor unit stopped function " , posted Fri 6 Jun 08:39
My reliable Trane A/C unit stopped working this week.The Circuit breaker on the A/C keeps tripping.I took the covers off of the outdoor unit, and cleaned it up.When I turn on the breaker I ... read more |
bsbets
 |
Replies (5) Re(1):13 yr old Trane Outdoor unit stopped fu - bsbets Re(1):13 yr old Trane Outdoor unit stopped fu - bsbets Re(1):13 yr old Trane Outdoor unit stopped fu - learner Re(2):13 yr old Trane Outdoor unit stopped fu - Houston204 Re(3):13 yr old Trane Outdoor unit stopped fu - Houston204
| |
 | "Trane XL 1400 line freeze? Filter location? " , posted Thu 5 Jun 22:11
Hi Guys, Have the above trane unit and we have noticed that the unit is not cooling as well as it should so I cleaned out the condenser today because it was really dirty. I noticed during the cleaning ... read more |
protech5
 |
Replies (5) Re(1):Trane XL 1400 line freeze? Filter locat - Houston204 Re(2):Trane XL 1400 line freeze? Filter locat - protech5 Re(3):Trane XL 1400 line freeze? Filter locat - Houston204 Re(4):Trane XL 1400 line freeze? Filter locat - protech5 Re(5):Trane XL 1400 line freeze? Filter locat - Houston204
| |
 | "outside unit/fan not working - steam? " , posted Thu 5 Jun 19:02
Hello all,I hope you can help me understand what may be happening to our outside unit. When it turns on, the contact is made, and it sounds like its going as normal. But the fan on top does not tu ... read more |
deltalima
 |
Replies (5) Re(1):outside unit/fan not working - steam? - Houston204 outside unit/fan not working - steam? - deltalima Re(1):outside unit/fan not working - steam? - Houston204 outside unit/fan not working - deltalima Re(2):outside unit/fan not working - steam? - Houston204
| |
 | "Trane 14xi and thermostat wiring " , posted Thu 5 Jun 09:44
I just got a new TH5220 thermostat for my Trane 14xi unit, I wired as Red and Red C to RedY: YellowC: BlueW: OrangeG: greenW2 whiteY2: Blackand proceed to configure ... read more |
datametsa
 |
Replies (2) Re(1):Trane 14xi and thermostat wiring - Houston204 Re(1):Trane 14xi and thermostat wiring - theduke03
| |
 | "What is my furnace " , posted Wed 4 Jun 21:45
I have a furnace in a new house I bought and cant seem to find any info about. it says Ultramax Olsen hcs2. can someone tell me is this a good model, and is it high eff. My House is 1800 Sq and it j ... read more |
kickrz
 |
Replies (8) Ñìîòðè: îôèãåíñêèé ïîðíî ñàéò! Âàì ïîíðàâèòüñ - DenMazila Re(1):What is my furnace - learner Re(2):What is my furnace - kickrz duct intact, goose unglued - dwcaveney Re(3):What is my furnace - learner read more
| |
 | "help installed new hvac system " , posted Wed 4 Jun 19:48
installed new goodman 95% furnace and 3ton ac and new a coilbut it doesnt seem to blow air through he vents very well.i checked for blockage at a coil.am i missing something?opened air coi ... read more |
candon329
 |
Replies (3) Re(1):help installed new hvac system - Jojo98 Re(1):help installed new hvac system - theduke03 Re(2):help installed new hvac system - 341
| |
 | "Central Air " , posted Wed 4 Jun 16:51
When I turned my Central Air conditioning on the suction line frosted up to the compresser??? What cuold be the cause>? Any help is greatly appreciated............Thanks, Scuba Steve ... read more |
scuba steve
 |
Replies (3) Re(1):Central Air - yeuem1 Re(2):Central Air - theduke03 Re(1):Central Air - hvac101
| |
 | "Help with HVAC system " , posted Wed 4 Jun 07:46
I have a HVAC system wich contains a water chiller and 3 fan coils , the water chiller runs with 9 Celsius Degrees on output . It has 100 Kw . The fan coils are 5Kw and my problem is that they are not ... read more |
Alexfreon
 |
Replies (3) Re(1):Help with HVAC system - Jojo98 Re(2):Help with HVAC system - alexfreon Re(3):Help with HVAC system - Jojo98
| |
 | "charging air conditioner " , posted Tue 3 Jun 21:58
I am new to installing air conditioners,and i am wondering when you are charging the system do you charge on the high side or low side. and are you to have the unit running. Do you want to get it to t ... read more |
jollyguy99
 |
Replies (4) Re(1):charging air conditioner - 341 Re(1):charging air conditioner - Its all good Re(1):charging air conditioner - burnerman Re(1):charging air conditioner - theduke03
| |
 | "what can I do " , posted Tue 3 Jun 19:36
Hi sir:I have RALB-030JAZ and It still working, do you think I better change another unit with 18 seer and do I have to change the low pressure line or not, now it is 3/4 in, thanksI h ... read more |
yeuem1
 |
Replies (4) Re(1):what can I do - theduke03 Re(2):what can I do - yeuem1 Re(3):what can I do - theduke03 Re(4):what can I do - learner
| |
 | "Chevy Truck 2004 V-8 " , posted Tue 3 Jun 11:37
Got a Chevy truck 2004 A/C system is not working. Was working last year and suspect was working through the winter when calling for defrost. When trying to add refrigerant there dose not seem to be an ... read more |
Dtech
 |
Replies (2) Re(1):Chevy Truck 2004 V-8 - theduke03 Re(2):Chevy Truck 2004 V-8 - Dtech
| |
 | "Fan shuts off when running AC " , posted Tue 3 Jun 11:17
I just started using my AC (not sure of the models etc.). The fan blowing the air through the house shuts down after it has been blowing only a few minutes and the unit outside keeps running. Any id ... read more |
gvr
 |
Replies (1) Re(1):Fan shuts off when running AC - theduke03
| |
 | "No A/C " , posted Mon 2 Jun 21:23
Hello, I have A Lennox G23 unit and the A/C will not come on. I turn the heat on and it works fine, but when I switch the thermostat to cool, the circuit breaker in the unit flips and the who ... read more |
kcroyals
 |
Replies (2) Re(1):No A/C - crapaud Re(1):No A/C - Houston204
| |
 | "Oiling Fan motor? " , posted Mon 2 Jun 20:58:
One of the outside units makes a loud screeching noise whenever the fan turns on outside. I bought the house as new construction in 2000? it is a Goodman A/C. Do I need to oil the Fan motor bearings? ... read more |
cool2wk
 |
Replies (6) Re(1):Oiling Fan motor? - theduke03 Re(2):Oiling Fan motor? - cool2wk Re(1):Oiling Fan motor? - Houston204 Re(2):Oiling Fan motor? - cool2wk Re(3):Oiling Fan motor? - mtcone read more
| |
 | "outside unit not kicking on " , posted Mon 2 Jun 18:06
Hey All-Replaced old RHEEM STAT with 7400d ( advised from reading forums here). Had some issue initially, as I was asked to help in the middle of the project.Long story short, I got it to ... read more |
tegaur
 |
Replies (27) try 190 =1 - dwcaveney Âèäåë êëàññíûé ïîðíî ïîðòàë. Ñòîèò çàöåíèòü. - DenMazila Re(1):outside unit not kicking on - theduke03 Re(2):outside unit not kicking on - tegaur Re(3):outside unit not kicking on - theduke03 read more
| |
 | "Trane xe 900 Fan does not turn " , posted Mon 2 Jun 15:03
Trane xe 900 Fan does not turn Made around 1999 . I have about 1800 Sq Ft TonwhouseI assume Trane xe 900 is 2 Ton unit Any ideas on Fan no spin, no cold air, Electricity seems fine< ... read more |
wkerns
 |
Replies (3) Re(1):Trane xe 900 Fan does not turn - cool2wk Re(2):Trane xe 900 Fan does not turn - Houston204 Re(1):Trane xe 900 Fan does not turn - cool2wk
| |
 | "Replacing a Capacitor " , posted Mon 2 Jun 04:06:
I need help replacing a capacitor on a Goodman unit: Model CKJ36-1AB Volts 208/230. The fan outside the house for the A/C was not running, and I could hear a humming sound. I started searching through ... read more |
cool2wk
 |
Replies (3) Re(1):Replacing a Capacitor - josh c Re(2):Replacing a Capacitor - cool2wk Re(2):Replacing a Capacitor - Houston204
| |
 | "changeover from a baystat 239 " , posted Sun 1 Jun 17:18
I have a trane weathertron baystat 239 would like to change it to a digital, non-programmable thermostat.Have had several leds.A.TRANE has a replacement THT0461 ,can not find a wiring diagram for it B ... read more |
pearce52
 |
Replies (1) Re(1):changeover from a baystat 239 - Houston204
| |
 | "New Honeywell RTH7500 " , posted Sun 1 Jun 16:41
I installed a new Honeywell RTH7500 thermostat today, replacing a manual Honeywell Model. The wires mapped out perfectly to the 7500 however when I turned on the unit, in Cool mode, heat was coming o ... read more |
mikep-sc
 |
Replies (8) Re(1):New Honeywell RTH7500 - mikep-sc Re(2):New Honeywell RTH7500 - Houston204 Re(3):New Honeywell RTH7500 - mikep-sc Re(4):New Honeywell RTH7500 - Houston204 Re(5):New Honeywell RTH7500 - mikep-sc read more
| |
 | "help " , posted Sun 1 Jun 16:09
mu hvac is not blowing cold air every thing is running but no cold air what to do ... read more |
eddiecouthen
 |
Replies (14) Re(1):help - Houston204 Re(2):help - cool2wk Re(3):help - learner Re(4):help - theduke03 Re(3):help - Houston204 read more
| |
 | "Replacing old stat with Honeywell RTH 6300 " , posted Sun 1 Jun 10:18:
Hello,This is my configuration....old then newTERM = WIREThe following wires were being used on old stat:The old stat appeared to not have Aux Heat.R=RED (JUMPERED) ... read more |
good1973
 |
Replies (3) Re(1):Replacing old stat with Honeywell RTH 6 - Houston204 Re(2):Replacing old stat with Honeywell RTH 6 - good1973 Re(3):Replacing old stat with Honeywell RTH 6 - Houston204
| |
 | "Lennox 10ACB - fan not running " , posted Sun 1 Jun 08:35
Good Morning -When I turned on my thermostat to engage my A/C this season, I hear a humming noise from my outdoor a/c unit but the fan doesn't seem to engage.The fan will spin freely w ... read more |
Dawn
 |
Replies (2) Re(1):Lennox 10ACB - fan not running - cool2wk Re(1):Lennox 10ACB - fan not running - theduke03
| |
 | "Experts, please help with insulated duct reco " , posted Sat 31 May 22:26:
Hello, I'm not an HVAC guy, but I'm hoping those of you who are can offer some advice on what I can use for a home project I'm working on. I'm converting a freezer into a kegerator that will remote ... read more |
RickDel
 |
Replies (2) Re(1):Experts, please help with insulated duc - dwcaveney Re(1):Experts, please help with insulated duc - Jojo98
| |
 | "Transformer " , posted Sat 31 May 19:17
How can you tell how many transformer you have. ... read more |
daddydee3
 |
Replies (5) Re(1):Transformer - burnerman Re(1):Transformer - theduke03 Re(1):Transformer - Jojo98 Re(1):Transformer - learner Re(2):Transformer - Houston204
| |
 | "Bryant A/C and ambient air " , posted Sat 31 May 17:39
I hope this forum isn't just for HVAC mechanics. If it is i'm sorry. I have a question. I have a five year old Bryant A/C/Furnace and a honeywell programmable thermostat. Originaly i just had a re ... read more |
inherited2002
 |
Replies (1) Re(1):Bryant A/C and ambient air - Houston204
| |
 | "installing vision 8000 " , posted Sat 31 May 16:36
I brought a honeywell visionPRO 8000 my wife took old out what wire goes where blue green orange yellow red white ... read more |
daddydee3
 |
Replies (3) Re(1):installing vision 8000 - theduke03 Re(2):installing vision 8000 - daddydee3 Re(3):installing vision 8000 - theduke03
| |
 | "Trane XE 1000/ XE80 blower- compressor prob. " , posted Sat 31 May 14:01
Hey folks- have a 8 year old xe1000 located on the sothern side of house- last year put in new fan. New Blower wheel six months ago.Unit has been working great- yesterday-hottest part of the day, ... read more |
handmeawrench
 |
Replies (3) Re(1):Trane XE 1000/ XE80 blower- compressor - theduke03 Re(2):Trane XE 1000/ XE80 blower- compressor - handmeawrench Re(3):Trane XE 1000/ XE80 blower- compressor - theduke03
| |
 | "2 compressors in 3 years....now bad AGAIN!!!! " , posted Fri 30 May 22:18
I'm glad I found this forum. We bought a brand new townhouse in Feb 2005, that my mom and sis live in (rent from us). Within a few months, once summer rolled around, the unit was giving us pro ... read more |
serenaMD
 |
Replies (5) Re(1):2 compressors in 3 years....now bad AGA - Jojo98 Re(1):2 compressors in 3 years....now bad AGA - Houston204 Re(2):2 compressors in 3 years....now bad AGA - yuri Re(3):2 compressors in 3 years....now bad AGA - serenaMD Re(4):2 compressors in 3 years....now bad AGA - theduke03
| |
 | "Hvac books " , posted Fri 30 May 21:29
New to Hvac and I'm still learning. Are there any books out there that show you step by step how to do it (charging, cleaning coils, repairing etc. ... read more |
Sondown
 |
Replies (4) Re(1):Hvac books - burnerman Re(1):Hvac books - Jojo98 Re(2):Hvac books - theduke03 Re(1):Hvac books - theduke03
| |
 | "Replacing A/C...add Heat Pump " , posted Fri 30 May 20:20
The compressor failed on our A/C (11 years old). We currently have two zones (1st and 2nd floors), gas furnace, and A/C.It seems that adding a Heat Pump to the A/C unit makes a lot of sense. ... read more |
indyhome
 |
Replies (3) Re(1):Replacing A/C...add Heat Pump - Houston204 Re(2):Replacing A/C...add Heat Pump - indyhome Re(3):Replacing A/C...add Heat Pump - Houston204
| |
 | "Need Help from Houston204 on Thermostat " , posted Fri 30 May 11:55
I need help from Houston204 on how to change my very old Honeywell round thermostat which control my baseboard heat and central A/C to a programmable LUX TX500.Could you show me how to connect ... read more |
PHILIPLEUNG366
 |
Replies (1) Re(1):Need Help from Houston204 on Thermostat - Houston204
| |