"a/c fan went out" , posted Sun 2 Nov 17:27user profileedit/delete messagepost reply


we had a warm day here yesterday and I turned the a/c on and about 20min or so I noticed it was getting warmer in the house so I went out back and the fan was not running but the compressor was so I shut the system down. now how do I check to see if the fan motor is bad or could it be something else? a/c is a 6 year old tempstar 4 ton

 


Replies:

Xenos
Webmaster



67.71.20.38

"Re(1):a/c fan went out" , posted Sun 2 Nov 19:28user profileedit/delete messagepost reply


Since the fan motor and compressor are powered off the same contactor. The most common thing would be the fan motor bearings. You could verify it is being powered.

Xenos.

The best way to escape a problem is to solve it.

 

 

hvt

206.172.131.45

"Re(2):a/c fan went out" , posted Sun 2 Nov 21:27:user profileedit/delete messagepost reply


Mike you could try turning the fan blade manually with a screwdriver, if there is any resistance to motion, the motor is finished, otherwise you have an electical problem, I would have the motor replaced..very common problem.
Actually mike, you may also have condenser fan motor cycling installed, did the motor not work at all?, did you haoppen to notice if it was cycling on/off?