| Bigjim | "Heat not working" , posted Sun 9 Nov 09:41:  
I have a Tempstar NULK100DH05 furnance that will not heat.. 1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch closes. 4. Draft inducer runs for 30 seconds to a minute you do not hear a gas hissing sound. The ignitor did glow, my furnace shuts down and goes into a lock out condition even if you turn your power switch off and on again the same cycle repeats with no heat. I do have a gas fire place that is working.
Bigjim with question and some answers
[this message was edited by Bigjim on Sun 9 Nov 10:10] | | Replies:
|
| Xenos Webmaster 
| "Re(1):Heat not working" , posted Sun 9 Nov 09:56  
BigJim as in Fishing ? if not oh well. As far as the furnace goes for some reason it’s not getting gas. Possible auxiliary limit but this one may be best serviced by a professional. Also make sure some fool isn’t playing a joke on you and turned off the meter.
Xenos.
The best way to escape a problem is to solve it.
|
| | Ad Mech | "Re(2):Heat not working" , posted Wed 12 Nov 20:15  
Bigjim No Ignitor glow tells me that you may have a bad HSI..check resistance across it..should read like a direct short..if it is good check limit switches like flame roll out, over temp, and pressure switch.. Good Luck