Sounds sound:) just verify the rated curent the Hum terminal is rated at 1 amp.
Xenos.
The best way to escape a problem is to solve it.
|
| | xenos Webmaster 
| "Re(3):Honeywell Humidifier on Trane XL80" , posted Tue 20 Jan 19:58  
If your on a well you may need to increase the restrictor size as its designed for 60Lbs water pressure.
Xenos.
The best way to escape a problem is to solve it.
|
| | kefxb24 | "Replaced restrictor screen" , posted Wed 21 Jan 09:43  
On city water will enough pressure.
Spent an hour taking apart the water valve. Even though this was new unit, it sat in the box for a few years before I got around to installing it. The screen on the water input side of the valve seemed to be causing the problem. Cleaned it with a little water and air, and we were good to go.
Thank you very, very much for such excellent advice and support. This is the best advice site I have ever found - really!
|
| | peewee27 | "Re(1):Replaced restrictor screen" , posted Thu 1 Feb 13:06  
quote: On city water will enough pressure.Spent an hour taking apart the water valve. Even though this was new unit, it sat in the box for a few years before I got around to installing it. The screen on
...
I am hoping you could help me.
I am having a problem with my solenoid valve on the HE360 as well. I ordered a new one just in case but haven't opened the package yet. Could you tell me how to remove the 2 black wires that leads from the solenoid to the connector? There are metal contacts on the end of these wires inside the plastic connector. I do not want to cut the wires if I do not have to. Can you disconnect it by inserting a small screwdriver into the plastic connector? I can figure out the rest unless you have some tips. Your help is greatly appreciated!!
DH
|
| | dp1 | "Re(2):Honeywell Humidifier on Trane XL80" , posted Tue 20 Jan 09:23  
Shouldn't you also fuse (in this case 1A if the humidifier draws 0.7A max) the 120VAC output from the furnace control board? This will protect the control board if the humidifier goes bad.
|
| | kefxb24 | "That is a good idea" , posted Tue 20 Jan 15:10  
Your suggestion is excellent. For a few pennies, you get a lot of protection.
Thanks for the suggestion.
|
|
|
|  |
|