winter heat no ac now! - http://www.hvacmechanic.com/ Forums


Original message

David1983

144.160.5.25

"winter heat no ac now!" , posted Tue 8 Jun 13:44user profileedit/delete messagepost reply


Replaced old thermostat with Honeywell CT87B. Heat worked last winter but now we get no AC. We have red, blue, white and green wires.

Connected Red to Rh
Green to G
White to W
Blue to Y...

First tried above and it didn't work..then

Per manual pic installed jumper from Rh to Rc...still no AC. Should BLUE still be on Y? How can I test if compressor works?

Havoc!

 


Replies:

xenos
Webmaster



67.70.16.52

"Re(1):winter heat no ac now!" , posted Tue 8 Jun 17:59user profileedit/delete messagepost reply


Y is the compressor wire.

Xenos.

The best way to escape a problem is to solve it.

 

TechMaster



24.73.11.62

"Re(1):winter heat no ac now!" , posted Tue 8 Jun 17:14user profileedit/delete messagepost reply


You do need the Rh-Rc jumper on a 4 wire system. You can try putting red, green, and blue together to see if the fan and compressor runs. If you do this with the thermostat removed and it runs then there's a problem with the thermostat.

Keep Cool!

 

 

David1983

144.160.5.25

"Re(2):winter heat no ac now!" , posted Wed 9 Jun 09:12user profileedit/delete messagepost reply


Thanks very much...went to Walmart bought new thermostadt, re-installed the same way and YES! YES! WE GOT AIR!

Havoc!