| JBechtel | "Lennox HP20 Compressor hums but won't turn" , posted Fri 18 Jun 21:40  
The compressor is getting 24 VAC. I'm thinking it's the run capacitor. How do I know it's bad?
| | Replies:
|
| JBechtel | "Re(1):Lennox HP20 Compressor hums but won't t" , posted Sat 19 Jun 07:13  
I meant the compressor relay is getting the 24VAC. This mornign I found out it's the relay. If I press it in with my finger it goes. Thanks for the help anyway.
|
| | Xenos Webmaster 
| "Re(2):Lennox HP20 Compressor hums but won't t" , posted Sat 19 Jun 16:42  
Your system may be off on a safety, as there 24 vac on Y and C if there is look at the safetys.
Xenos.
The best way to escape a problem is to solve it.
|
| cesarin78801 | "Re(1):Lennox HP20 Compressor hums but won't t" , posted Fri 18 Jun 23:17  
brother the compressor doesn't run with 24 volts if you meant to say 240 and it doesn't run i could be locked to find out if the capacitor is bad,get the uf rating of the existing capacitor get a meter that will read "uf's"and it can be 10% (+)or(-)if is not with in the limits replace it if it is get a hard start kit(potential relay and start capacitor)
|
|
|
|  |
|